All electrical appliances using mains voltage have to provide at least 2 levels of protection to the user. This is to ensure that if one of the protection layers were to fail, there is the back-up of the second layer still in place. This makes electrical equipment very safe to use. Appliances can be Class 1 or Class 2. When PAT testing, it is important to first identify the Class of the appliance as Class 1 appliances are tested differently from Class 2 appliances.




CLASS 1

Here the protection is provided by a combination of insulation and use of the mains Earth. It is best shown by referring to an electric fire that has been taken apart.

In the open plug the three wires connecting to the LIVE, NEUTRAL and EARTH pins. Inside the fire, the brown LIVE wire and the blue NEUTRAL wire connect to a plastic connector. The green/yellow Earth wire connects to the metal case of the fire.

The user is protected from electric shock by the plastic insulation of the connector. This holds the LIVE and NEUTRAL wires in place and prevents them from touching the metal case of this electric fire. This plastic insulation of the connector is known as basic insulation.

If this basic insulation were to fail, say due to excessive movement of the cable where it touches the metal case then the user of the fire can receive an electric shock if not for the fact that the EARTH wire is present.

By connecting to the metal case of the electric fire, the EARTH wire keeps all this metal at EARTH potential. What this means is that it is impossible to get an electric shock even when the metal case of the fire is connected directly to the LIVE voltage. In practice a fuse would blow either in the plug or the main fuse box to protect the user.

In summary, in Class 1 appliances the user is protected by a combination of basic insulation and the provision of an EARTH connection, thus providing two levels of protection. When PAT Testing Class 1 appliances, the Earth Continuity and Insulation Resistance tests are carried out.

CLASS 2

In a Class 2 appliance, the user is protected by at least two layers of insulation. For this reason, Class 2 appliances are also known as Double Insulated. They do not require an Earth connection.


This is best shown by looking inside a Class 2 electric drill which has been opened up. Inside one can see that as well as the plastic connector providing basic insulation, there is additional insulation provided by the plastic enclosure of the drill.
 
The user is therefore protected by two separate layers of insulation. When PAT testing Class 2 appliances, just the Insulation Resistance test is carried out.

Class 2 appliances are always indicated by the double box symbol on the rating plate.


IDENTIFYING CLASS I & CLASS II APPLIANCE

As the PAT testing carried on Class 1 and Class 2 appliances differ, it is important to identify one from the other. There is no other area of PAT testing that causes more confusion than this and there are many myths surrounding this. It will be informative to list some of these.

If there is a fuse in the plug, then it must be Class 1.
It is made of metal so it must be Class 1
The case is plastic so it must be Class 2
It has a three core cable so it must be Class 1
The plug has a metal Earth pin so it must be Class 1

None of the above statements is a fool-proof way to identify Class I and Class II appliances and some are quite misleading.

The easiest rule to apply is the one below.

If the rating plate has a double box then the appliance is Class 2. If it does not then it is Class 1.

Example - Kettle

The rating plate on this kettle clearly has no "double-box" symbol, so using our rule, it must be Class 1. The Earth connection from the plug is terminated on the outside metal casing of the heating element. When PAT testing this kettle the Earth Continuity and Insulation Resistance test has to be carried out.




Example - Plug-top power supply

The rating plate on this Plug-top transformer clearly shows the "double box" symbol, so this is a Class 2 appliance. Note that it has a plastic Earth pin, as this is not required for Class II. (Not all Class 2 appliances have a plastic earth pin). Just the Insulation Resistance test has to be carried out during PAT testing.






Example - Mains extension



The rating plate on this extension is moulded in the plastic. It clearly does not have a "double-box" symbol, so it must be a Class 1. When PAT testing this extension lead the Earth Continuity and Insulation Resistance test has to be carried out.




Example - Table lamp

The rating plate on this table lamp clearly shows the "double-box" so it is a Class 2 appliance. (Note that this is a Class 2 appliance that is largely in a metal enclosure). The bulb holder is made of plastic and provides the required double insulation. Just the Insulation Resistance test has to be carried out during PAT testing.





Example - Desk fan

The rating plate for this fan not only does not have a "double-box" symbol, it also says that the appliance must be earthed. So this is clearly a Class 1 appliance. Note that it does not have any user accessible metal.





Example - Metal Lamp

If this metal lamp had a rating plate, then it would be a Class 1 appliance as it has an earth point on the lamp holder. However, as the rating plate is missing, this would have to be failed.









Are Class 1 and Class 2 appliances just as safe?

As both have 2 levels of protection built in, they are both safe for general use.

However with Class 1 an appliance, one of the layers of safety is provided by the earth connection. For this to be effective, the wiring in the building has to be inspected regularly to check that the Earth in the mains socket is correctly taken to the local earth potential. This is usually picked off the Earth sheathing of the mains cable coming into the premises, or by driving a local stake into the ground. So Class 1 appliances depend on the external wiring in the building to fully provide the 2 levels of protection.

Class 2 appliances however always provide 2 levels of protection irrespective of the status of the wiring installation. Both layers of protection are built into the design making Class 2 appliances are a lot safer than Class 1 appliances.

 

14 comments:

  1. What does shield symbol mean in plug top power supply pic? Have a MCT Transformatoren gmbh indoor water fountain. Lead is obviously waterproof but is transformer plug? It is 240V 50-60 hz 12V 20VA SIT20/240/12-00-40B TS115 IP24. It is class 2 - double box symbol with plastic earth pin and carries the shield symbol too as in your image (plug top power supply). Can send pic.

    ReplyDelete
    Replies
    1. Very unlikely that plug is also waterproof unless plugged into IP68 enclosure or socket. Do you have a picture?

      Delete
  2. Does Class I require a fuse in the appliance itself?

    ReplyDelete
    Replies
    1. Class I just means that the user is protected from shock by the use of an Earth. Some Class I products have fuses in the appliance itself and some don't. This is decided as part of the safety design and testing process.

      Delete
  3. I have a jetdryer hand dryer machine similar to the dyson, it has the double insulated logo on the label on the machine yet it has a earth pin on the top plug with a fuse in the top plug, i say its a class I, but has double square double insulated logo.

    ReplyDelete
    Replies
    1. Not sure what you mean by 'top plug'. Class II appliances need to be fused to protect from a fault causing a fire.

      Delete
  4. Hello. Trying to test commercial oven Falcon model- G3106. It does metal body and 3pin earthed cable and no "double box" symbol on the plate so I was testing it as Class 1 . It does failed on earth test. Could it be Class " ??? or there is something wrong with it. thx

    ReplyDelete
    Replies
    1. Agree with you that this sounds like Class 1. Looks like ti has a metal body. When it fails the Earth test what is the reading? Is it a marginal fail (say 0.15 ohms) or much higher? The failure needs investigating.

      Delete
  5. If theres no rating plate,or CE mark on a toaster should it be tested or, as i think,binned.

    ReplyDelete
  6. This was very useful, thanks!

    ReplyDelete
  7. Does a metal housed device connected to an external power supply with 24VDC output to the device, also the GND line connected to EARTH to be tested for protective bounding? This seems a Class 1 device but no mains voltage is entering into the device.

    ReplyDelete
    Replies
    1. I presume that there is only 2 connectors on the 24VDC supply to this device and when you say GND line you mean the 0V connection.

      If the external supply is Class II then there is no need for testing for protective bonding because the 0V line is actually isolated from actual GND.

      If the external supply is Class I AND the 0V is connected to EARTH, then test the power supply and the device together for protective GND.