All electrical appliances using mains voltage have to provide at  least 2 levels of protection to the user. This is to ensure that if one  of the protection layers were to fail, there is the back-up of the  second layer still in place. This makes electrical equipment very safe  to use. Appliances can be Class 1 or Class 2. When PAT testing, it  is important to first identify the Class of the appliance as Class 1  appliances are tested differently from Class 2 appliances.
CLASS 1
Here  the protection is provided by a combination of insulation and use of  the mains Earth. It is best shown by referring to an electric fire that  has been taken apart.
In the open plug the three wires connecting  to the LIVE, NEUTRAL and EARTH pins. Inside the fire, the brown LIVE  wire and the blue NEUTRAL wire connect to a plastic connector. The  green/yellow Earth wire connects to the metal case of the fire.
The  user is protected from electric shock by the plastic insulation of the  connector. This holds the LIVE and NEUTRAL wires in place and prevents  them from touching the metal case of this electric fire. This plastic  insulation of the connector is known as basic insulation.
If this  basic insulation were to fail, say due to excessive movement of the  cable where it touches the metal case then the user of the fire can  receive an electric shock if not for the fact that the EARTH wire is  present.
By connecting to the metal case of the electric fire, the  EARTH wire keeps all this metal at EARTH potential. What this means is  that it is impossible to get an electric shock even when the metal case  of the fire is connected directly to the LIVE voltage. In practice a  fuse would blow either in the plug or the main fuse box to protect the  user.
In summary, in Class 1 appliances the user is protected by a  combination of basic insulation and the provision of an EARTH  connection, thus providing two levels of protection. When PAT Testing Class 1 appliances, the Earth Continuity and Insulation Resistance tests are carried out.
CLASS 2
In  a Class 2 appliance, the user is protected by at least two layers of  insulation. For this reason, Class 2 appliances are also known as Double  Insulated. They do not require an Earth connection.
 This is best  shown by looking inside a Class 2 electric drill which has been opened  up. Inside one can see that as well as the plastic connector providing  basic insulation, there is additional insulation provided by the plastic  enclosure of the drill.
This is best  shown by looking inside a Class 2 electric drill which has been opened  up. Inside one can see that as well as the plastic connector providing  basic insulation, there is additional insulation provided by the plastic  enclosure of the drill.The user is therefore protected by two  separate layers of insulation. When PAT testing Class 2 appliances, just  the Insulation Resistance test is carried out.
Class 2 appliances are always indicated by the double box symbol on the rating plate.
IDENTIFYING CLASS I & CLASS II APPLIANCE
As  the PAT testing carried on Class 1 and Class 2 appliances differ, it is  important to identify one from the other. There is no other area of PAT  testing that causes more confusion than this and there are many myths  surrounding this. It will be informative to list some of these.
If there is a fuse in the plug, then it must be Class 1.
It is made of metal so it must be Class 1
The case is plastic so it must be Class 2
It has a three core cable so it must be Class 1
The plug has a metal Earth pin so it must be Class 1
None of the above statements is a fool-proof way to identify Class I and Class II appliances and some are quite misleading.
The easiest rule to apply is the one below.
If the rating plate has a double box then the appliance is Class 2. If it does not then it is Class 1.
Example - Kettle
The  rating plate on this kettle clearly has no "double-box" symbol, so  using our rule, it must be Class 1. The Earth connection from the plug  is terminated on the outside metal casing of the heating element. When  PAT testing this kettle the Earth Continuity and Insulation Resistance  test has to be carried out.
Example - Plug-top power supply
The  rating plate on this Plug-top transformer clearly shows the "double  box" symbol, so this is a Class 2 appliance. Note that it has a plastic  Earth pin, as this is not required for Class II. (Not all Class 2  appliances have a plastic earth pin). Just the Insulation Resistance  test has to be carried out during PAT testing.
Example - Mains extension
The  rating plate on this extension is moulded in the plastic. It clearly  does not have a "double-box" symbol, so it must be a Class 1. When PAT  testing this extension lead the Earth Continuity and Insulation  Resistance test has to be carried out.
Example - Table lamp
The  rating plate on this table lamp clearly shows the "double-box" so it is  a Class 2 appliance. (Note that this is a Class 2 appliance that is  largely in a metal enclosure). The bulb holder is made of plastic and  provides the required double insulation. Just the Insulation Resistance  test has to be carried out during PAT testing.
Example - Desk fan
The  rating plate for this fan not only does not have a "double-box" symbol,  it also says that the appliance must be earthed. So this is clearly a  Class 1 appliance. Note that it does not have any user accessible metal.
Example - Metal Lamp
If  this metal lamp had a rating plate, then it would be a Class 1  appliance as it has an earth point on the lamp holder. However, as the  rating plate is missing, this would have to be failed.
Are Class 1 and Class 2 appliances just as safe?
As both have 2 levels of protection built in, they are both safe for general use.
However  with Class 1 an appliance, one of the layers of safety is provided by  the earth connection. For this to be effective, the wiring in the  building has to be inspected regularly to check that the Earth in the  mains socket is correctly taken to the local earth potential. This is  usually picked off the Earth sheathing of the mains cable coming into  the premises, or by driving a local stake into the ground. So Class 1  appliances depend on the external wiring in the building to fully  provide the 2 levels of protection.
Class 2 appliances however  always provide 2 levels of protection irrespective of the status of the  wiring installation. Both layers of protection are built into the design  making Class 2 appliances are a lot safer than Class 1 appliances.

What does shield symbol mean in plug top power supply pic? Have a MCT Transformatoren gmbh indoor water fountain. Lead is obviously waterproof but is transformer plug? It is 240V 50-60 hz 12V 20VA SIT20/240/12-00-40B TS115 IP24. It is class 2 - double box symbol with plastic earth pin and carries the shield symbol too as in your image (plug top power supply). Can send pic.
ReplyDeleteVery unlikely that plug is also waterproof unless plugged into IP68 enclosure or socket. Do you have a picture?
DeleteDoes Class I require a fuse in the appliance itself?
ReplyDeleteClass I just means that the user is protected from shock by the use of an Earth. Some Class I products have fuses in the appliance itself and some don't. This is decided as part of the safety design and testing process.
DeleteI have a jetdryer hand dryer machine similar to the dyson, it has the double insulated logo on the label on the machine yet it has a earth pin on the top plug with a fuse in the top plug, i say its a class I, but has double square double insulated logo.
ReplyDeleteNot sure what you mean by 'top plug'. Class II appliances need to be fused to protect from a fault causing a fire.
DeleteHello. Trying to test commercial oven Falcon model- G3106. It does metal body and 3pin earthed cable and no "double box" symbol on the plate so I was testing it as Class 1 . It does failed on earth test. Could it be Class " ??? or there is something wrong with it. thx
ReplyDeleteAgree with you that this sounds like Class 1. Looks like ti has a metal body. When it fails the Earth test what is the reading? Is it a marginal fail (say 0.15 ohms) or much higher? The failure needs investigating.
DeleteIf theres no rating plate,or CE mark on a toaster should it be tested or, as i think,binned.
ReplyDeleteSafest option is to fail it.
ReplyDeleteThis was very useful, thanks!
ReplyDeleteDoes a metal housed device connected to an external power supply with 24VDC output to the device, also the GND line connected to EARTH to be tested for protective bounding? This seems a Class 1 device but no mains voltage is entering into the device.
ReplyDeleteI presume that there is only 2 connectors on the 24VDC supply to this device and when you say GND line you mean the 0V connection.
DeleteIf the external supply is Class II then there is no need for testing for protective bonding because the 0V line is actually isolated from actual GND.
If the external supply is Class I AND the 0V is connected to EARTH, then test the power supply and the device together for protective GND.
This comment has been removed by the author.
ReplyDelete